Trying to diagnose 308 A/C charging issue.. | FerrariChat

Trying to diagnose 308 A/C charging issue..

Discussion in 'Technical Q&A' started by greg328, Apr 22, 2011.

This site may earn a commission from merchant affiliate links, including eBay, Amazon, Skimlinks, and others.

  1. greg328

    greg328 F1 Rookie

    Nov 17, 2003
    4,209
    Austin, TX USA
    Full Name:
    Greg
    77 GTB. I've retrofitted a Sanden compressor, new drier, expansion valve, lines, etc. Running R134. Did this years ago, always has run well.

    I've charged the system before--I have a small leak somewhere, so I need to recharge every couple summers. This month I tried again, but the compressor won't suck in the freon. It does indeed click on. I have the fittings properly fastened, I am using professional gauges. I've screwed down the connectors on the hoses onto the line fittings--they are indeed joined.

    With car running, AC on, I open up the lines, (hi and low side) but the freon will not suck in! Yes, the compressor is running. It's a 4-year old Sanden, has always worked fine.

    I also tried a different method, using a top-tap lo-side hose attached with a color-coded gauges (Autozone special!). Still won't suck in.

    Thoroughly puzzled--would welcome any ideas/input..
    Greg in Houston
     
  2. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    What is the ambient temperature and what are the high and low side pressures reading while the compressor is engaged? What are the pressures when the engine is off?

    TomB
     
  3. greg328

    greg328 F1 Rookie

    Nov 17, 2003
    4,209
    Austin, TX USA
    Full Name:
    Greg
    Can't remember the exact numbers, but with engine off, the numbers were higher. Once the car and AC were on, the gauge reflected very low numbers. They did change.
    It was about 85 degrees in my garage.
    Greg
     
  4. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    For very rough numbers, at 80 degrees the refrigerant might be at 90 psi. Once a working compressor is started up the high side will go to somewhere near 200 and the low side will go down to maybe 30. If you start with 90 in the can, it will be drawn to the low side of 30. The low side has to be lower than the source for the transfer of fluid to happen. Again, these are very inaccurate numbers, for demonstration purposes only, but you get the idea.
    If the high side isn't going up, and or the low side isn't going down, that would be a start to diagnosing what's going on.

    TomB
     
  5. Jagbuff

    Jagbuff Formula 3

    Jan 13, 2004
    2,267
    Site of US F1 Race!
    Full Name:
    Franck
    Does it have binary pressure switch?
    Are you using the gauge properly (not trying to be a wise a$$) but I assume you are using the yellow line to lead to lo-pressure side which requires opening the valve? Have you tried a cheapo direct single line to the lo-pressure side? BTW, did you evacuate the system before recharging?
     
  6. Paul_308

    Paul_308 Formula 3

    Mar 12, 2004
    2,345
    Pressure in the source can is higher than in the car so it doesn't need to be 'sucked' in. It just flows in if there is a path through the gauge set. You may have a (common) stuck expansion valve. Needing a top-off every couple years doesn't mean a small leak, it's normal leakage. Since you don't do this often, likely you have forgotten a small procedural detail, like turning the freon can upside down so you get liquid and not gas.
     
  7. Buggin

    Buggin Karting

    Dec 8, 2006
    169
    Farmersville, TX
    Full Name:
    die langsame
    May not have any bearing on the issue, but are you running any kind of particulate filter in the AC system? If the compressor is clicking on, but not drawing, there may be some kind of clog in the system. On another note, what kind of shape are your hoses in? Do any of them show any cracking or age? I have seen systems clog due to degradation of the hoses, where a clog will occur and block the flow of refrigerant even if the filter is new, or not installed.

    You may also want to do a current check on the switches and solenoids related to the system. Sorry I cant tell you what current is good, and which is bad. What I will usually do is compare what I have in hand, to a new one.

    Issue with that is unless you got the parts from a local parts house then you may not be able to compare yours with another one.

    Hope any of that helps.
     
  8. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    The pressure in the source can is only higher than the low side pressure if the compressor is working properly. If the compressor is not working the pressures will be equal. If the engine is hot the low side pressure could be higher then the can. Could be the system is full and and an additional charge will make things worse. Knowing the pressures would go along way towards figuring out what is really going on. Chrysler used to produce a great book with many different readings and what they meant.

    Of course an evacuation and recharge with the recommended amount of refrigerant is always best.

    And don't forget that as the system leaks through the years you're losing oil also, and that should be topped up as well.

    TomB
     
  9. PAP 348

    PAP 348 Ten Time F1 World Champ
    Lifetime Rossa Owner

    Dec 10, 2005
    100,232
    Mount Isa, Australia
    Full Name:
    Pap
    My thoughts exactly. :D:D

    I didnt post this morning because I wanted to confirm with our a/c specialist at work. :D:D

    The first thing he said was "it may be a stuck or REALLY restricted TX valve (expansion valve)". :):)

    So I would recover the gas from the system, then remove the TX valve and inspect. :):)
     
  10. greg328

    greg328 F1 Rookie

    Nov 17, 2003
    4,209
    Austin, TX USA
    Full Name:
    Greg
    Guys, I appreciate all the responses, very helpful. The car is currently parked off-site, I was doing this last weekend, so I'm working from memory.

    The pressures, when running and engine on, were something like 99psi hi side, and 30psi lo side, pretty certain. With engine shut down, and gauges still attached, the lo side shot up, but I think that's just internal gauge pressure, nothing to do with the car, right? Again, this is from memory, and may be incorrect.

    The expansion valve is new, only a couple years old. So is the dryer. The lines from compressor to condenser up front are new. Everything in the system is relatively new, so that's why this situation surprises me.

    I do have an AC vacuum, maybe I'll vacuum the entire system, and inspect the ex. valve.

    Thanks again, I'll get the car back here, and report my results ASAP.
    Greg
     
  11. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    99 on the high side and 30 on the low side could indeed indicate a low charge. If the expansion valve was stuck shut the low side would be low and the high side would be high, as in the refrigerant is being compressed but has no place to go. If the expansion valve is stuck open the high side will be low because there is nothing keeping the pressure up.
    I think you might be back to your original question as to why the system apparently not accepting juice.
    This could likely be a problem with what ever you're using for hoses/connector valves. With the engine off you could connect the low side hose without the can on the end and slowly open the valve on the compressor. Refrig. should escape. This would tell you that you are connected to the system.

    We await your next response.

    TomB
     
  12. greg328

    greg328 F1 Rookie

    Nov 17, 2003
    4,209
    Austin, TX USA
    Full Name:
    Greg
    Tom,
    with engine off, hoses attached, I can bleed refrigerant along with a bit of compressor oil, out of the system. There's a little schrader valve located right above the middle freon hose on the gauge set, you can push it to bleed the system. Yes, some of the can's contents escaped, but the oil must be coming from the compressor, right? This tells me the system is hooked up correctly.

    ??

    Greg
     
  13. Paul_308

    Paul_308 Formula 3

    Mar 12, 2004
    2,345
    Hope that was said in jest.

    I use 30# cans and know from experience they must be upside down to exude liquid refrigerant, not needing the compressor to be on when doing so. That also how one overfills the system and a overpressure switch is in the system. The can's handles at the top are also stands so it can sit on a scale for precise measurement. Placed right side up and only gas escapes the hose which cannot overpower the system to fill it.
     
  14. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    Gregg-
    Disregard the high side for a moment- with the compressor spinning, when you open the valve on the supply can does the low side pressure change at all? It the set up is correct to feed more into the system the pressure in the can needs to be higher then the pressure in the low side.
    The most useful thing to do once you figure this out would be to would be to evacuate the system and start from scratch. I believe that tool rental places will rent you an electric vacuum pump. Again, too much will do almost as much to performance as too little.
    The theories here are really basic- solutions to AC problems usually follow a pretty logical path.
    I agree turning the supply can upside down is a more efficient way to charge the system, and can more easily result in an over-charge, but you will eventually get the refrig. out of the can and in your car as a gas, it just takes a while.

    TomB
     
  15. PAP 348

    PAP 348 Ten Time F1 World Champ
    Lifetime Rossa Owner

    Dec 10, 2005
    100,232
    Mount Isa, Australia
    Full Name:
    Pap
    Your TX valve can still be stuck or restricted, whether it was replaced 4 yrs ago or not. If there is crap in the system or a/c doesnt get used much it can stick. :):)

    I asked another a/c guy at work today and he said the though the same thing, a TX valve issue. :):)

    Obviously easier to diagnose with the car in front of you, but we all share the same thoughts on the subject so I would look there first. :):)

    But whatever man, just saying. :):)
     
  16. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    I'm wrong about something of value every day, but the expansion valve theory doesn't explain why he can't get the juice to flow into the system, which was the original question. If the pressure in the can is higher then the low side, shouldn't it go in?

    TomB
     
  17. greg328

    greg328 F1 Rookie

    Nov 17, 2003
    4,209
    Austin, TX USA
    Full Name:
    Greg
    Tom--exactly. I'm using a new can of freon, new can tap, new gauges, even the hose fittings to the compressor are recent. Can't figure out why the freon won't flow in.

    Maybe I will pull a vacuum, I do have a AC vac. I just hate to waste any freon already in there.

    If I do evacuate the system and pull a vacuum, do I need to add compressor oil again?
    How do I know the level of compressor oil left in there? Doesn't it remain in the system, even if gas is released?

    Greg
     
  18. Paul_308

    Paul_308 Formula 3

    Mar 12, 2004
    2,345
    Are you sure you punctured the seal in the top of the can?

    YES, an unknown quantity of oil mixed with the refrigerant is lost [My lawyer made me add this next part] when you go to an certified ac shop to have your existing gas pulled with a recovery system. Newer recovery systems can add oil without having to open the lines.
    OR NO Some will ignore the oil loss. I think that's playing with fire.
    OR NO Some will add a back a small amount of oil. That's playing with a much smaller fire.

    A few compressors additionally have an external non-pressurized crankcase reservoir which needs a fixed amount of oil. An oil volume stamped on the compressor refers to this and NOT to refrigerant oil...I can't speak to your specific Sanden compressor.

    For a full start-from-scratch A1 driveway job, you must remove most ALL the oil. Using shop air, blow all remaining oil out of both hoses, turning the compressor by hand a few times as it will host much oil. Add oil. Then remove moisture and non-undesirable contaminants in the system by pulling an overnight vacuum. ReCharge.
     
  19. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    I mostly agree. Unless you drain the compressor you never really know. For lack of a better plan, when removing the compressor is not practical or possible, I do add an once or 2 of oil.
    It's a tough call. Refrig. recycling machines have a means to separate and measure the oil when you drain the system. However, you never know about past history such as how much seeped out with the leak.
    If you have a vacuum pump, by all means start from scratch. If you've been losing and adding for a few years it would be nice to have a base line from which to gauge what's going on.
    Besides, if you can evacuate the system then you know you're hose/fitting connections are good.

    TomB
     
  20. PAP 348

    PAP 348 Ten Time F1 World Champ
    Lifetime Rossa Owner

    Dec 10, 2005
    100,232
    Mount Isa, Australia
    Full Name:
    Pap
    Heya mate, I will try my best to explain and to be a little more clear.

    When you have a blocked TX valve, you can actually put a/c refridgerant into the system. I should have said that earlier sorry.

    The needles wont move, which makes you think the a/c system is not taking refridgerant.

    But, in fact it is. Refridgerant goes from the compressor, to condensor, to drier then onto the TX valve.

    If you keep trying to fill the a/c system with refridgerant(which you think its not taking any, but it is) the refridgerant will reach the blocked TX valve and then start to "back fill" the a/c system with refridgerant which will eventually go back to the compressor as a liquid and you run the chance of 'lugging' the compressor, or blowing out the seals or actually damaging the compressor.

    So............if everything is connected properly, the pressure in the freon can is higher than that of the low pressure side gauges, the can has actually been "punctured"................then I (and my guru a/c mates) can only think of a blocked/restricted TX valve as the problem Greg is having with the freon he is adding is not making his gauges move/system is not taking gas.

    As suggested, I would recover the a/c gas. Remove the TX valve to inspect. It may be seized or have some crap in there. We have this issue at work all the time, TX blockages and some that seize also, but more TX valves with blockages.

    Inspect/sort the TX valve, add 50ml of oil into the system then vac down and add the exact amount of freon needed for your 308.

    Start the car, turn on the a/c and check its performance. :eek::eek:

    I hope this helps explain it a little better mate. It is A LOT easier saying it in person. I consulted my 2 a/c specialists at work again about this. I really only wanted them to help me try and explain it typing on the computer for you here. :D:D
     
  21. tomberlin

    tomberlin Formula Junior
    Silver Subscribed

    Apr 9, 2005
    854
    Bethesda
    Full Name:
    tom berlin
    Pap,

    I'm with you.

    TomB
     
  22. PAP 348

    PAP 348 Ten Time F1 World Champ
    Lifetime Rossa Owner

    Dec 10, 2005
    100,232
    Mount Isa, Australia
    Full Name:
    Pap
    Not a problem mate, I probably should have tried to explain earlier if it wasnt so hard to try and get across clearly.

    It took me ages to type that post trying to word it correctly so it made a little bit of sense. :eek::eek:

    It may not be the issue, but sure sounds like it. Especially if there is nothing stopping the freon from entering the system. :):)
     
  23. POLO35

    POLO35 Formula Junior

    Feb 21, 2005
    792
    Treasure Coast Florida
    Full Name:
    MATT
    Well everyone else has a theory....so i figured I'll chime in. Possibility one that the hose you are using is not opening the schrader valve far enough to charge the system....Possibiltiy two is that the valve-hose you are using is old and has "swollen" internally and choked off, preventing you from charging the system.....BTW both of these happened to me. I wound up going to harbour freight and buying a cheap set of gauges.
     
  24. PAP 348

    PAP 348 Ten Time F1 World Champ
    Lifetime Rossa Owner

    Dec 10, 2005
    100,232
    Mount Isa, Australia
    Full Name:
    Pap
    Both possible, of course. :):)

    But if you read post #10 and #12, I think he doesnt have an issue with the gauges being connected properly and working properly as he states the pressures change when he starts and turns the a/c off. :):)
     
  25. Lawrence Coppari

    Lawrence Coppari Formula 3

    Apr 29, 2002
    2,192
    Kingsport, TN
    Full Name:
    Lawrence A. Coppari
    Ditto the business about the Schrader valve not being open far enough to charge. I have several cars that take R12. Two charge with no problem. However, the good old 328 had a valve that was not opening enough when the recharge fitting was screwed on. I ended up slicing a sliver off the rubber seal inside the screw on brass fitting. This enables the valve to be forced open a wee bit more and makes all the difference. It charges up nicely now.

    Stay cool!
     